Latch Alarms

Latch Alarms

With the latch alarms feature, the alarm will not clear until an operator clears the alarm. Customers can enable the latch alarms to any High High or Low Low sensor for SCADA devices. The latch alarms feature ensures that someone is looking into an alarm that has been triggered and is not missed. Once an alarm is manually cleared, it will still fall back into the alarm state, on the next poll, should it still be outside of the parameters set in place.

Once the latch alarm feature has been enabled, each sensor can be configured. To configure the latch alarm.

1. Select Configure Alarm in the pull-down menu on the site display.

Image 1318

2. Select the sensor for the latch alarms to be enabled.

Image 1319

3. Toggle on Latch to enable.

Image 1320

    • Please note, that this is only applicable for High High and Low Low alarms.

    4. Once a set latch alarm has been triggered, it will show as an alarm on the site display, as usual. However, will not clear with the next poll, should the alarm set point be back in normal status. It will also not clear with next poll even if it transitions to any other type of alarm, as well. Example: it is in high high latch alarm state, and the next poll value that comes in is in the “high” or “low” range, it will not transition to those other alarm states. It will remain in the state it was in requiring someone to clear it.

    Image 1321

    5. The alarm will now have to be manually cleared. Select the alarm and in the Current Alarm Tab and select Clear.

    Image 1322

    6. Enter in notes if needed, and clear as usual.

    Image 1327

    7. Now the alarm will be cleared.

    Image 1323

      • Please note, the alarm will be triggered again on the next poll, if the sensor is still outside of the set configurations.

      8. The Low Low Latch / High High Latch sensor will appear in the search criteria, in the alarms page. 

      Image 1324

      9. Latch alarms can be identified by hovering over the sensor in the Summary Tab, as well as the Live Data Screen.

        Summary Tab

        Image 1325

        Live Data Screen

        Image 1326